15A to 20A Adapter Cord?

Posted: Sat Apr 11, 2009 10:29 pm
by Endo
I've seen the 20A to 15A adpater cord. Does anyone know if someone sells a 15A to 20A, or would that be illegal?

Easy enough to make, but I thought I'd ask.

Re: 15A to 20A Adapter Cord?

Posted: Sun Apr 12, 2009 8:42 am
by JohnB
If you are moving up to 20a why not just install a 20a plug on your machines power cord?

Re: 15A to 20A Adapter Cord?

Posted: Sun Apr 12, 2009 9:48 am
by chas
Endo wrote:I've seen the 20A to 15A adpater cord. Does anyone know if someone sells a 15A to 20A, or would that be illegal?

Easy enough to make, but I thought I'd ask.
Unless 20A outlets are different in Canada, all the 20A outlets I have seen in the US will take 20A or 15A plugs. So of you want to plug a 15A plug into a 20A outlet and run the machine in 20A mode it will work, no adapter necessary.

Re: 15A to 20A Adapter Cord?

Posted: Sun Apr 12, 2009 2:02 pm
by Endo
chas wrote: Unless 20A outlets are different in Canada, all the 20A outlets I have seen in the US will take 20A or 15A plugs. So of you want to plug a 15A plug into a 20A outlet and run the machine in 20A mode it will work, no adapter necessary.
Good to know. That seems like the simplest option since I can switch back to a 15A outlet easily if I change locations.

Re: 15A to 20A Adapter Cord?

Posted: Mon Apr 13, 2009 7:02 pm
by Endo
I check the 20A outlets at Home Depot. They take both 15A and 20A plugs.

I'll have to switch my home wiring from 14 to 12 gauge to go to 20A and also install a 20A breaker, but I was just wondering if the stock 15A plug and cord on my machine can take 20A so I wouldn't need to change it. I can't tell if the cord is 14 or 12.

Maybe I'll just play it safe and do like everyone else and install a 20A cord and plug and put a 15A pigtail on when needed.

Re: 15A to 20A Adapter Cord?

Posted: Mon Apr 13, 2009 9:53 pm
by JohnB
Why the sudden lust for 20a? I thought you were satisfied with the 15A performance.

Re: 15A to 20A Adapter Cord?

Posted: Tue Apr 14, 2009 9:46 am
by Endo
JohnB wrote:Why the sudden lust for 20a? I thought you were satisfied with the 15A performance.
I'd like to get more predictability of when the steam boiler heater will come on.

I find that if the steam boiler heater is on and I choose the riight sized tip area I can balance the pressure increase with the pressure descrease, and steaming is very predictable. On my Silvia I could see on my PID display that the steam temp/pressure was steady within 2 deg C for as long as I wanted to steam (a good balanced system).

As you know, on the 15A Mini Vivaldi, the steam boiler heating gets interrupted due to the brew boiler taking priority. On the small boiler Mini, the pressure can go very low if this happens. Going 20A gets rid of this interruption.

On the flip side, on the Mini it may also turn out to be impossible keep the element "on" all the time during steaming since it may be too powerful for the boiler size (and require too big a tip area). So I may be stuck swinging back and forth in this pressure deadband. Big commercial DB machines have huge steam boilers so they don't experience this swing . That's why I don't have the same trouble making microfoam on the commercial LMs.

Probably not an issue unless you are trying to make perfect microfoam.

Re: 15A to 20A Adapter Cord?

Posted: Tue Apr 14, 2009 12:17 pm
by JohnB
Endo wrote:
On the flip side, on the Mini it may also turn out to be impossible keep the element "on" all the time during steaming since it may be too powerful for the boiler size (and require too big a tip area). So I may be stuck swinging back and forth in this pressure deadband. Big commercial DB machines have huge steam boilers so they don't experience this swing . That's why I don't have the same trouble making microfoam on the commercial LMs.

Probably not an issue unless you are trying to make perfect microfoam.
Its not an issue on the S1V2 with the 2.5 litre boiler either.

Re: 15A to 20A Adapter Cord?

Posted: Wed Apr 29, 2009 8:28 pm
by fiddlefly
Well, this is an old thread but i figure i'd pitch in...
Since i converted my v1's cord to 15 by changing the plug, and all of them machines seem to have an inside switch, I'd guess it is safe to assume that the cord is safe... for 20 on all... no?

Re: 15A to 20A Adapter Cord?

Posted: Thu Apr 30, 2009 8:01 am
by JohnB
Since they are designed as 20A machines I'd have to agree.

Re: 15A to 20A Adapter Cord?

Posted: Sat May 02, 2009 11:32 pm
by fiddlefly
This just in to my world...
http://www.orphanespresso.com/index.php ... cts_id=870
could this work?? :bounce:

Re: 15A to 20A Adapter Cord?

Posted: Sun May 03, 2009 9:11 am
by JohnB
fiddlefly wrote:This just in to my world...
http://www.orphanespresso.com/index.php ... cts_id=870
could this work?? :bounce:
For what? You already have a 110v machine don't you?

Re: 15A to 20A Adapter Cord?

Posted: Sun May 03, 2009 9:40 pm
by fiddlefly
to be able to run it 20 a safely in a 15 a outlet...

Re: 15A to 20A Adapter Cord?

Posted: Sun May 03, 2009 11:14 pm
by MDL
Perhaps there is some confusion here.

There is no safe way to draw 20 amps through a 15 amp circuit. Some might feel that it is OK to use a 15 amp outlet if the wiring is 20 amp, but I think that is still being penny wise and pound foolish since a 20 amp outlet costs little more than a 15 amp version.

Mark

Re: 15A to 20A Adapter Cord?

Posted: Mon May 04, 2009 7:59 am
by JohnB
Spend the money on a dedicated 20A circuit.

Re: 15A to 20A Adapter Cord?

Posted: Thu May 28, 2009 10:03 pm
by Endo
Endo wrote: I was just wondering if the stock 15A plug and cord on my machine can take 20A so I wouldn't need to change it. I can't tell if the cord is 14 or 12.
Still wondering....is it safe to flip the switch and draw from a newly installed 20A outlet through the pre-installed 15A plug? The only part I'm worrying about is the 15A cord itself (not the machine). Not sure if the 15A cord uses 12 gauge or not.

Re: 15A to 20A Adapter Cord?

Posted: Fri May 29, 2009 10:07 am
by MDL
You can presume that 15A cords are not adequate for 20A use. No manufacturer is likely to over-build in that manner; it is too expensive and opens them to potential product liability issues. In addition, the majority of cords have the information on them (at least in the USA). Look with care at the cord and see what it says (I must admit that I have not checked to see what the cord on my 20A Vivaldi says).

It is possible that the Vivaldi's are built with 20A cords (but different plugs) since they have the switch to run at either amperage. Again, I would look along the entire length of the cord to see what, if anything it says.

Good luck,
Mark

Re: 15A to 20A Adapter Cord?

Posted: Fri May 29, 2009 3:38 pm
by Endo
Actually, Chris Coffee just wrote me back and told me the 15A plug and cord is fine for 20A. They used to simply switch the plug from 15A to 20A but now they just sell the 20A version and give you a convertor cord if you want 15A (saves them time that way). They said just to make sure everything on the opposite side of the pulg (outlet , wall wires, breaker, etc) are 20A.

But since mine came directly from LaSpaziale with the dedicated 15A plug and cord, I'm still wondering. I'll have a close look tonight to see if anything is written on the cord.

Re: 15A to 20A Adapter Cord?

Posted: Fri May 29, 2009 9:57 pm
by Endo
OK. Found a few stamps on the cord. One says 14awg3xc. I assume this means 14 gauge wire annd max 15A?

Now I'm pretty sure it's NOT safe to run it in 20A mode. Does anyone know for sure?

How about all you owners with the 20A plug. What's stamped on your cord?

Re: 15A to 20A Adapter Cord?

Posted: Sun May 31, 2009 6:11 pm
by JohnB
Endo wrote:OK. Found a few stamps on the cord. One says 14awg3xc. I assume this means 14 gauge wire annd max 15A?

Now I'm pretty sure it's NOT safe to run it in 20A mode. Does anyone know for sure?

How about all you owners with the 20A plug. What's stamped on your cord?
12AWG/3xc & its a very beefy cord that you wouldn't mistake for 14g/15a. Looks like the cord on my mig welder.

Re: 15A to 20A Adapter Cord?

Posted: Sun May 31, 2009 6:43 pm
by SnowDragon
14 Gauge = 15 Amps
12 Gauge = 20 Amps
10 Gauge = 30 Amps
08 Gauge = 40 Amps
06 Gauge = 65 Amps

So if you want to run 3 mini's on one plug, you need 6 Gauge. :twisted:

If you try to run on 20 amps with the 14 Gauge cable, you may run into trouble, including damage to the machine. :bom:

Re: 15A to 20A Adapter Cord?

Posted: Sun May 31, 2009 8:09 pm
by Endo
Looks like I'll need to switch the whole cord and plug when I go to 20A. Not a huge deal I imagine, although I haven't yet looked to see how it's attached on the inside.

Seems the Mini Vivaldi 2 from CC all come with the thicker 20A cord but the Mini Vivaldi that comes direct from LaSpaziale can have either a 15A cord OR a 20A cord. Good to know.

Thanks MDL for mentioning to check the cord itself.

Hey SnowDragon....those warm espressos must taste pretty good way up there in Nunavut on those cold nights. Bet there aren't many other Vivaldi owners too near by! :smile:

Re: 15A to 20A Adapter Cord?

Posted: Sun Jun 07, 2009 9:27 am
by SnowDragon
Yes...Warm...Good idea.

Yes I probably am the only MV2 owner so far up north.

It's been a year now since I got my baby in and have no regrets.

Next stop, roasting.

Re: 15A to 20A Adapter Cord?

Posted: Sun Jun 07, 2009 8:59 pm
by Endo
SnowDragon wrote:Next stop, roasting.
Yes....I would imagine this would be a necessity! :shock: